bath house
ronlow00
Minnesota
I am currently working on an aquatic center that was built in the 70's and is now being remodeled. The building consists of a concessions area, concessions storage, mens and womens bath rooms and changing rooms, and staff rooms. I am trying to figure if their is any reasion that the existing receptacles have to be GFCI protected. Where can I find any Codes on GFCI protection about the building if any.
Re: bath house
All bathrooms residential or commercial require any receptacles to be gfci protected,however you are not required in commercial bathrooms to have an outlet.If this is a remodel you may or maynot be grandfathered in.Best to call the inspector for his advice.
Re: bath house
210.8 (B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1), (2), and (3) shall have ground-fault circuit-interrupter protection for personnel:
(1) Bathrooms
(2) Rooftops
(3) Kitchens
Exception: Receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with the applicable provisions of Article 426.
Re: bath house
I go with Jim call the AHJ and see what he wants.Guess it depends on extent of remodel.If you open it most times it has to meet current code requiremants