If there is a thread for this already please point me in the right direction.
I am having a difficult time convincing my fellow inspectors that all receptacle circuits in the bathroom must be 20amp. (or am I the one whoe needs convincing)
This is my logic,
210.11(C)(3) Says at least one 20amp branch circuit shall be provided to supply bathroom reeptacle outlet(s). The exception refers to 210.23(A)(1) and (A)(2) with the exception for (A) refering you back to 210.11(C)(3) and to me saying the outlet(s) will be 20amp.
210.8(A)(1) says they have to be GFI protected. ALL OF THEM.
210.52(D) lets you know where the required location is for a basin.
I have failed a particular Electrical rough for not having all the Receptacles in the bathroom on 20amp ckt or ckts. Due to my interpretation above.
Am I missing something??
Thanks for your help
Always wanting to make a fair and honest inspection, :wink:
Andrew
I am having a difficult time convincing my fellow inspectors that all receptacle circuits in the bathroom must be 20amp. (or am I the one whoe needs convincing)
210.11(C)(3) Says at least one 20amp branch circuit shall be provided to supply bathroom reeptacle outlet(s). The exception refers to 210.23(A)(1) and (A)(2) with the exception for (A) refering you back to 210.11(C)(3) and to me saying the outlet(s) will be 20amp.
210.8(A)(1) says they have to be GFI protected. ALL OF THEM.
210.52(D) lets you know where the required location is for a basin.
I have failed a particular Electrical rough for not having all the Receptacles in the bathroom on 20amp ckt or ckts. Due to my interpretation above.
Am I missing something??
Thanks for your help
Always wanting to make a fair and honest inspection, :wink:
Andrew