If you are asking if the 20 amp circuit required for the bathroom receptacle can also feed the bathroom light, then the answer is yes, if you only feed one bathroom.
If you loop the bathroom receptacle circuit to more than one bathroom then it can only feed the receptacles. See 210.11(C)(3) 2005
you guy beat me, man i'm a slow typer.
(edit to add last line)
Chris