Seems the NFPA can't nail down the English on this one.
1996: 210-52(d): In dwelling units, at least one wall receptacle outlet shall be installed in bathrooms adjacent to each basin location. Bathroom receptacle outlets shall be supplied by at least one 20-ampere branch circuit. Such circuits shall have no other outlets.....
1999: 210-11(c)(3): In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets. (followed by exception).
2002: 210.11(C)(3): In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets. (followed by exception).
2005 and 2008 and 2011: 210.11(C)(3): In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets. (followed by exception). [notice the deletion of the word 'the' between 'supply' and 'bathroom']
2014: 210.11(C)(3): In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets. (followed by exception). [notice the addition of the word 'a' between 'supply' and 'bathroom'. This change is NOT highlighted in gray, nor is it mentioned in the current Errata!]