- Location
- Massachusetts
Not necessarily. It can be done. 210.11(C)(3) Exception.
Now that I look at that section I think you and I are talking apples and oranges.
I don't see that section allowing the 14 AWG tap of the 20 amp circuit.
Not necessarily. It can be done. 210.11(C)(3) Exception.
Now that I look at that section I think you and I are talking apples and oranges.
I don't see that section allowing the 14 AWG tap of the 20 amp circuit.
Now that I look at that section I think you and I are talking apples and oranges.
I don't see that section allowing the 14 AWG tap of the 20 amp circuit.
Really?
310.16 says 14 AWG copper is rated 20 amps, and for many applications we can use it at 20 amps.
The only reason 14 AWG can not be used at 20 amps in this application is 240.4(D).