It need not be on the same circuit as the required-near-the-sink receptacle, but it must be GFCI protected, and either it cannot supply anything but bath receptacles (in more than one bath is okay), or it cannot feed anything outside of this bathroom.So I can't use another circuit for a wall mounted TV?
what about a receptacle for a towel warmer that has to be on its own circuit?
and I won't even bring up a whirl pool tub pump receptacle
The way I read 210.11(C)(3) is no outlets outside of the bathroom can be on the bathroom circuit, but nowhere does it say other circuits can not feed other outlets in the bathroom?, just they have to be GFCI protected, as per 210.8
Of course.
There is nothing in the code that prevents you from adding receptacles in the bathroom from other circuits in the dwelling. As long as you have at least one 20 amp circuit dedicated to supplying the bath circuit requirements. If the dedicated circuit supplies anything besides the GFCI in the bathroom it must be one of the following, only one of the following and nothing else:
Other receptacles in any bathrooms in the dwelling
-or-
Other outlets in the same bathroom
It looks pretty cut and dry to me in 210.11(C)(3)
I have had inspectors say otherwise they site the wording "shall be provided to supply bathroom receptacle outlet(s)"
I just came across this situation this week. Customer wanted a receptacle for a lighted mirror in an existing bathroom. There happened to be couple of switches for the exhaust fan/ light right above the desired location. Three feet of 14-2, a cut in box and a GFI......mission accomplished.
Inquiring Minds Want to Know, where the switches on the dedicated circuit for the bathroom or were they a different circuit?
The circuit I tapped into was not the required 20A bathroom circuit. It was a general purpose lighting circuit. No violation IMHO
What else was on that circuit you tapped ? If it was a dedicated circuit just for this bathroom then fine. Or if it was only bathroom receptacles fine. If it was not one of them and had any others loads from other rooms then while the original receptacle is grandfathered in you would have created a violation by adding the new one.Did the install today and I grabbed the load side of the GFI in the bathroom.
Thanks for all of the different views posted to this topic.
What else was on that circuit you tapped ? If it was a dedicated circuit just for this bathroom then fine. Or if it was only bathroom receptacles fine. If it was not one of them and had any others loads from other rooms then while the original receptacle is grandfathered in you would have created a violation by adding the new one.
Personally i do not see any danger but nec might have been violated.