Tainted Senior Member Location New York Occupation Engineer (PE) Nov 22, 2022 #1 Does a bathroom exhaust fan need to be included in the calculation or does the 3VA/sqft cover it already? Where do you apply bathroom exhaust fans in the calculation? Is it considered a appliance fastened in place?
Does a bathroom exhaust fan need to be included in the calculation or does the 3VA/sqft cover it already? Where do you apply bathroom exhaust fans in the calculation? Is it considered a appliance fastened in place?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 22, 2022 #2 See 220.12(A) or 220.14(J) for nondwelling and dwelling occupancies for motors that are 1/8 hp or less. Note these are 2020 code citations.
See 220.12(A) or 220.14(J) for nondwelling and dwelling occupancies for motors that are 1/8 hp or less. Note these are 2020 code citations.