Bathroom GFCI

Status
Not open for further replies.

lle

Member
I usually run a circuit for a bathroom GFCI then jump to a second bathroom GFCI. I usually end up with two or three receptacles on this circuit.

I was told that I can NOT take this GFCI circuit from one bathroom to another, that I have to run a new circuit for each bathroom.

Is this a new code change?
 
Re: Bathroom GFCI

210.11(C)(3) and Exception . If there are only bathroom outlets on the circuit, it is permitted to supply more than one bathroom on the circuit.

Edit: Forgot to add I am going off of the 2002 NEC.

[ May 26, 2005, 08:10 AM: Message edited by: wirenut1980 ]
 
Re: Bathroom GFCI

No, there's no real change, you can still put all the bathroom receptacles on the same circuit, so long as those receptacles are all that's on that circuit.

The wording in the 2005 has been tweaked to allow the exception to be used in mulitiple bathrooms, provided each bathroom gets it own circuit.
 