Re: BATHROOM POWER
If the receptacle outlets in all the bathrooms are on the same 20 amp circuit, that is compliant with the NEC. But that one circuit is not permitted to power the lights, fans, or any other component - receptacles only. The reference is NEC 210.11(C)(3). If a single circuit powers one bathroom and no other room, then that circuit can supply all outlets in that bathroom (i.e., lights, fans, etc.).
You can certainly pay to have more work done, but it?s clear that you are looking for another way. So what can you do? It depends on how the contract (or other work agreement) was written. If nothing was written, then you have no recourse for compelling the contractor to make a change.