Bathroom receptacle requirement met?

Status
Not open for further replies.
Re: Bathroom receptacle requirement met?

Yes, being this is a small vanity. The code seems to call for a wall receptacle. I interpret to my advantage this potential recp. to be in the wall of the cabinet.

Placing a receptacle in this area uses the exception in kitchens. However I am not sure why. There is no minimum height which makes me wonder why we need an exception to install in the side of a cabinet.
 
Re: Bathroom receptacle requirement met?

210.52 (D) The receptacle outlet shall be located on a wall OR PARTITION that is adjacent to the basin OR BASIN COUNTERTOP

My guess is it complies.
 
Status
Not open for further replies.
Top