Re: Bathroom vanity GFI protected receptacles
I hope test takers are reading this.
Seeing that we are in this together, I'm not going to bash anyone. I will give what is written in the hardcover NEC -AKA Handbook. NEC 210.52D: In dewelling units, atleast one wall receptacle outlet shall be installed in bathrooms within 900mm (3ft) of the outside edge of each basin. the receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
Make note: That the Hardcover (AKA handbook) has explanations. Which "Can" be enforced "if" the AHJ see fit. I "NEVER SIAD THAT WHAT THE AHJ RULED ON IS RIGHT. I JUST SAID THAT WHAT HE RULED ON CAN BE DUE TO THE EXPLANATION PRESENTED IN THE 210.52(D) EXPLANATION.
The explanation: Section 210.52(D) requires one wall receptacle in each bathroom of a dwelling unit to be installed adjacent (within 36 in.) to tje washbasin. This receptacle is required in addition to any receptacle that may be part of any luminaire or medicine cabinet. If there is more than one washbasin, a receptacle outlet is required adjacent to each basin location. If the basins are in close proximity, one receptacle outlet installed between the two basins might satisfy this requirement.
It's perfectly understandable that you guys are against what is clearly written in the NEC. Just make note, that I'm not against what you guys are saying. I'm clearly writting what can be enforced by the AHJ--if he/she so chooses.
iwire, it's great that you can present the fact that an AHJ can only enforce a ruling if it's adopted into law. Yet isn't this true for any law.
To apprentices: Make not that an AHJ can rule according to what's written in the NEC, and laws adopted by locality. But, this does not mean you can't agrue the ruling. Clearly, I'm being misunderstood. Heck, we put receptacles in between two sink often--if the customer wants to save money, and if it meets code requirements. But, what the explanation presents on article 210.52(D) is fact. If in close proimity--how can you argue against truth.
Example: If you have two sinks, and you plan to put a receptacle between the two, but noticed that the receptacle is out of proimity to meet NEC 210.52(D), then what makes what was written wrong.
By the way. The Hardcover does give more information than the softcover. But I should have said this: Although it gives more information (information being pictures, and explanations), the articles will not change in any form, regardless of which NEC book you have.