Hospital They r remodeling a bathroom in a hospital not in a patient room it is a public restroom. It does not have any showered just a toilets and a sink. Is it required to a a receptical. 2014 code I can't find anything in the code book that says it has to be other then maybe 210.60 similar occupancies thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In general bathrooms do not need a receptacle however if one is installed then it needs to be gfci protected. I believe if this is a standard bathroom then no gfci is needed
 

kwired

Electron manager
Location
NE Nebraska
210.8(B) Covers GFCI protection for non dwelling units -

Bathrooms is the number one item on the list.

Art 100 definition of a bathroom:

An area including a basin with one or more of the following: a toilet, a urinal, a tub, a shower, a bidet, or similar plumbing fixtures.

A toilet and a basin in the same area is a bathroom.

210 Part III doesn't require receptacles in a non dwelling bathroom, but GFCI protection is still required if you put any in.
 