bathtub lights

Status
Not open for further replies.
article 410.10d outlines the zone in which you cannot use an assortment of fixtures within thatzone. then it goes on to say that any fixture within that zone and TO 8 ft mustshall be marked vaperproof or watertite.
The first part did not exclude recessed fixtures or surface mount fixtures which in my case would have been vaperproof.
I understand that article to mean that I can use a surface mount that is vaperproof witin the aformentioned zone.Am i correct or do i read "up to" to mean higher than 8 ft.?
 
[FONT=Arial, Helvetica, sans-serif]By Mike Holt, for EC&M Magazine [/FONT]

[FONT=Arial, Helvetica, sans-serif]Q1. What are the requirements for installing fixtures in bathroom?[/FONT]
[FONT=Arial, Helvetica, sans-serif][/FONT]​
[FONT=Arial, Helvetica, sans-serif]A1. No part of chain-, cable-, or cord-suspended luminaires, track luminaires, or ceiling paddle fans can be located within 3 ft horizontally and 8 ft vertically from the top of the bathtub rim or shower stall threshold. [/FONT]​
[FONT=Arial, Helvetica, sans-serif][/FONT]​
[FONT=Arial, Helvetica, sans-serif]Luminaires located within the actual outside dimensions of a bathtub or shower to a height of 8 ft from the top of the bathtub rim or shower threshold must be marked for damp locations. Where subject to shower spray, the luminaires must be marked for wet locations [410.10(D)]. [/FONT]​
 