using your peak 5 kw, 20 A, size for 25
assume avg draw is 50%
size for 3 days
ahr = 3 x 24 x 50% x 25 = 1275 ahr, use 1400 (+10%)
dc bus ~ 2 sqrt2/Pi x 240 = 216
assume 12 vdc 100 ahr std ups battery
216/12 = 18 battery per string for 100 ahr
so need 1400/100 = 14 strings or 14 x 18 = 252 batteries
you need to split the system into 2 pnls
norm and emergency
service into norm with branch to ups then to emerg pnl
battery vol ~ 350 cu ft or ~ 16' long x 3' deep x 8' tall
ups ~ $7k
batteries ~ $18k
plus freight, install, etc...freight alone might be a few k
plus pnl work and any space requirements