Can someone explain to me why there are batteries used for switch gear? ICAN make a guess but are not sure why.
Not just after a power failure, the batteries are the sole source of trip and closing power for the breakers.Basicly DC Systems are used in switchgear applications for breaker control in the event of a power failure
A motor or solenoid charges the closing springs, the act of closing the breaker charges the trip springs.,charging both trip and closing springs,
I was once told by an old timer that a DC closure of a motor breaker or large starters was faster and more positive than AC.it slams it home, thus less arcing.
dick
Can someone explain to me why there are batteries used for switch gear? ICAN make a guess but are not sure why.
Basicly DC Systems are used in switchgear applications for breaker control in the event of a power failure ,charging both trip and closing springs,DC is used almost exclusively for tripping while some closing springs are AC as well.DC is used for montoring,system interface,UPS back up.
I was once told by an old timer that a DC closure of a motor breaker or large starters was faster and more positive than AC.it slams it home, thus less arcing.
dick
Until someone 'turns off' the battery charger. I am always amazed by the number of facilities I visit that do not monitor and alarm their DC bus voltage.DC control power from a battery rack is as uninterruptable as you can get.
Until someone 'turns off' the battery charger. I am always amazed by the number of facilities I visit that do not monitor and alarm their DC bus voltage.
Just as a bit of opposing view, there are times where breaker control power can be derived from the line voltage of the gear, depending on the sequences (or lack thereof) that are expected when the power is out.
Some basic gear can be supported with CPT's and never need the additional functionality of a stored DC source.
Usually, yes.Great information ...
Our batterries are along side the switchgear , there are 24 in the rack [48vdc] that need maintenance [water added when low ] it has a battery charger connected to them with a status meter.
From the post that have been made that is the only power used to open or close,trip a breaker in the switchgear ?
Not really, the clearing times are determined by the relay setings and the breaker speed. Only if the batteries were off line or too low a voltage so the breakers won;t trip would it be an issue.Also It would have alot to do with the clearing time with the switchgear and hrc should the batterries be in poor or fair condition ?
To a point yes, for example a 125VDC trip coil is required to be abe to trip the breaker at 90VDC. That is something we test on all our breakers, not many people do for some reason.Would the breakers be able to trip with low dc power?
Alarm systems are very common for this. Always ensure the charger is set at the proper float voltage and maintain your batteries per IEEE Std 450We will have to have some one monitor the status meter or maybe install a remote meter.
Thanks again for all the tips with this.
Just as a bit of opposing view, there are times where breaker control power can be derived from the line voltage of the gear, depending on the sequences (or lack thereof) that are expected when the power is out.
Some basic gear can be supported with CPT's and never need the additional functionality of a stored DC source.
Even the Capacitor Trip Devices have to be replaced every few years because the internal capacitors degrade.
That's why we stock them.Basler also makes a nice electronic "cap trip" device for replacements.