I have inherited dozens of existing buildings to determine if the current f/a systems have enough battery capacity to carry the NFPA 72 requirements. I can do all the math for the 24 hours at idle and 5 minutes at alarm state. What I can't seem to get a good answer on is how to accurately measure the actual current draw of the system so I can then do that math.
I have measured Ah on the 120v side and then converted to the 24v by math, but that seems to be wrong, I have tried measuring Ah the 24v side with the A/C off, but that doesn't match the previous math. I assume I need to find Ah on the load side of the power supply, but that is not always easy with integrated power supply units.
I of course, do not have any of the original battery calculations or other design info.
I am working typically with Simplex 4100u and Siemens MXL-IQ.
:-?
I have measured Ah on the 120v side and then converted to the 24v by math, but that seems to be wrong, I have tried measuring Ah the 24v side with the A/C off, but that doesn't match the previous math. I assume I need to find Ah on the load side of the power supply, but that is not always easy with integrated power supply units.
I of course, do not have any of the original battery calculations or other design info.
I am working typically with Simplex 4100u and Siemens MXL-IQ.
:-?