Battery Charger OCP

Status
Not open for further replies.
Here is the nameplate on the charger. It is not a new charger. They want it moved to another building and I'm thinking it was on 208V but not sure since the building has two services.

It is a microprocessor controlled, so I would check with the manufacturer on compatibility. The last “new” one I put in was about five years ago.
 
Math looks good.
Not continuous load. You said one forklift. No way could that be continuous load by my knowledge of forklift operation. ;)
i.e. not full current for 3 hours plus.
I'll be running #8 copper anyway and the 50A breaker is the same price as the 40A, so I will just cover my bases.
Thanks!
 
Status
Not open for further replies.
Top