Sounds logical. #8cu on 50a?So 8K/208 =38.4A
Continuous load?
Last edited:
Sounds logical. #8cu on 50a?So 8K/208 =38.4A
Continuous load?
It is a microprocessor controlled, so I would check with the manufacturer on compatibility. The last “new” one I put in was about five years ago.
The PDF shows that 208v will work fine.It is a microprocessor controlled, so I would check with the manufacturer on compatibility. The last “new” one I put in was about five years ago.
Math looks good.So 8K/208 =38.4A
Continuous load?
I'll be running #8 copper anyway and the 50A breaker is the same price as the 40A, so I will just cover my bases.Math looks good.
Not continuous load. You said one forklift. No way could that be continuous load by my knowledge of forklift operation.
i.e. not full current for 3 hours plus.