the ATS is located at the service and the genset is located 250' away. we would simply be breaking the two wire start contacts in the ATS to prevent the generator from starting during the night. the control circuit is on 12 volts and is generator by the battery on board the generator. just need a battery operated timer switch. with a 24 hour clock and a dry set of contacts to make happen.
What brand of generator and ATS is this?
For example, a Generac generator will typically start on its own if the utility AC voltage falls below a threshold level for more than a certain duration. After a warm-up time the controller in the generator will pull wire 23 down from 12VDC to ~0VDC which then causes the ATS to transfer to standby power. If you want to prevent the generator from starting you'd need to run another control wire to the generator for implementing this function (using a relay, etc.).
Yes, I believe power from the POCO is usually necessary to move the transfer switch to the utility position. For example, in Generac ATS schematics the utility supply is rectified to provide DC current for the solenoid that switches the ATS to the utility position. So if the utility does not come back online after the generator is shut down, then the ATS will still be in the standby position if the generator comes on.Hey guys, while we are all figuring out the time issue we are forgetting one problem that it will create. I was told that it is not good practice to start a generator under load, hence why there is a lag between power out generator start, and power back on. How will the restart be addressed, if the transfer switch is still in emergency position, and the generator output breaker is on?
With a Generac, perhaps a separate contactor in line with the generator output could keep the generator disconnected until the generator pulls wire 23 down near 0VDC (which indicates it's ready to supply power).