iggy2
- NEw England
We are designing a STANDBY power system for a community building. The SPS will power everything except the laundry and the electric water heater. The SPS will power all the normal lighting. There are battery units for egress lighting. There is no emergency power system. The presumption is that the community building will be used by local residents to gather in the event of an extended power outage, since their apartment electric heat/cooking/lighting will be out.
Should the battery units be powered by the generator, or no???
If powered by the generator, the battery units will turn off as soon as the transfer switch transfers - and there will be no egress lighting. (Of course, the 'normal' lights will be on, but they will not be powered from an emergency system.)
If not powered by the generator, on a power failure, the battery units will run for 90 minutes, then die, and again - there will be no egress lighting.
This is in MA, so 2009 IBC is in effect.
"1006.1 Illumination required. The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied."
"1006.3 Illumination emergency power. The power supply for means of egress illumination shall normally be provided by the premises' electrical supply. In the event of a power supply failure, an emergency electrical system shall illuminate all of the following areas:..."