Working on a friend's cabin. Mix of bx and romex, new 200 amp service installed by a licensed contractor recently. He has a GFCI outlet in the bathroom which does not trip on test so he purchased a new one and asked if I would change it out. Installed the new on using the line connections on the device. New one does not trip either. Plugged in my tester, no lights at all and test button has no effect. Checked voltage with my Fluke, polarity correct, 124.7 vac hot to neutral & hot to ground, continuity between neutral and ground. Golly gee whiz? Only thing I need to check is perhaps this was added to existing bx old wiring, could that make a difference?