What is the benefit of a 3 phase 208 panel to a single phase 240?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
What is the benefit of a 3 phase 208 panel to a single phase 240?
Sent from my iPhone using Tapatalk
What is the benefit of a 3 phase 208 transformer to a single phase 240?
What is the benefit of a 3 phase 208 panel to a single phase 240?
Sent from my iPhone using Tapatalk
That response changes my whole perspective on what was being asked. I thought some kind of conversion from 208 three phase to 120/240 single phase was being asked about. But if it was just a question of advantages of having 208/120 three phase compared to having 120/240 single phase, then yes the ability to operate three phase loads is at the top of the list.You can operate 3-phase loads.
The job I have now the mdp is feeding a 480vlt 400 amp panel. .A 75 amp breaker feeds a 75kva to step it down to the 208 panel. I am not sure what the panel is rated for, there is no main on it. Which is my next question I do have a small lite load do I need a main cb?
Sent from my iPhone using Tapatalk
What is the benefit of a 3 phase 208 panel to a single phase 240?
Sent from my iPhone using Tapatalk
Only if there is a neutral conductor run from the secondary. 3-wire single phase and 4-wire three phase systems are required to have secondary conductor protection, or where otherwise and primary protection times voltage ratio is greater than ampacity of secondary conductors. As always, details, details, details.Even though you don't need secondary protection for the tranny, you have to protect the secondary conuctors. 240 or 208, you should have an MCB.
208 75kVA transformer requires 200+ amps. With the same power at a higher voltage, the amp output should be cut in half. Well that's what p=iv states.If I feed 3 phase 208v @ 100 amps into a step up transformer (75kva) the secondary side at 480v will be how many amps?
Actually the current would be half if we were converting 240 volts to 480 volts. @ 208 volts to 240 volts the ratio is about 2.31:1 instead of 2:1.208 75kVA transformer requires 200+ amps. With the same power at a higher voltage, the amp output should be cut in half. Well that's what p=iv states.
480?Actually the current would be half if we were converting 240 volts to 480 volts. @ 208 volts to 240 volts the ratio is about 2.31:1 instead of 2:1.
Yes, that is what I intended to say there.480?