bedroom circuits

Status
Not open for further replies.

edwin1

Member
Does each bedroom in a dwelling require its own afci circuit? A recent inspector red tagged a new home rough-in because there were more than 10 devices on one of the afci circuits. There were two afci ciciuts pulled in the house, one for the master bedroom and one for two smaller bedrooms in the other end of the house.
 
Re: bedroom circuits

I learned a cute trick from a residential contractor.He uses 1 afci for the smokes and ceiling fans and fixed lights,and the other for all the bedroom receptacles.Takes 1 home run from the nearest smoke the other from closest receptacle.Helps if the fault is from homeowners plugged in stuff,just unplug everything,if it resets then its there problem.Nothing in NEC even calls for 2 afci one meets code
 
Re: bedroom circuits

NEC 210.11 states that loads for branch circuits are to be computed in accordance with 220.3. 220.3 states that the minimum receptacle load is 3 VA per square foot. If you have a 15A circuit, it's good for 600 sq.ft.
 
Re: bedroom circuits

This may draw some flack but here goes anyway :)

Take as an example, in a residential application, Using ten 15 amp circuits from the same panel to supply general purpose outlets in a 3,000 sq. ft. area. That would average out to aproximately 300 sq. ft. per circuit. Now, if you use one of those circuits, protected with an AFCI breaker to supply a 600 sq. ft. bedroom, you would be in violation of 210.11(B).

Am I wrong?
 
Re: bedroom circuits

I think that this is not a violation of 210.11(B). Here is how I see it:
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Your total load for this set of general purpose loads is 3000 x 3 = 9000 VA</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">You supply a 600 square foot bedroom with one circuit. That is worth 3 x 600 = 1800 VA.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">That leaves 9 circuits to supply the remaining 7,200 VA, giving each an average of 800 VA.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The total load on Phase A (presuming it is the one with the big bedroom) is 1800 + 4 x 800 = 5000 VA. This is equivalent to 33 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The total load on Phase B is 5 x 800 = 4000 VA. This is equivalent to 42 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">This amount of difference in the current in the two Phases (i.e., 9 amps) is not significant. If, for example, the loads are perfectly balanced at one moment in time, and if at that moment your wife turns on an 1200 watt hair dryer, then the current in the phase that powers that hair dryer will exceed the current in the other phase by more than 9 amps.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">I don?t think that the concept of ?evenly proportioned,? as cited in 210.11(B), was intended to be measured and verified to the minutest degree of precision. A reasonable attempt to balance the loads, for example by using breakers from top to bottom and not skipping every other breaker, should be sufficient for code compliance.
 
Re: bedroom circuits

Well, I agree that it is not the intent that "evenly proportioned" be measured to a minute degree of precision. I agree that a reasonable attempt to balance the load is all that is expected. And this requirement is not something that I would put on my list of things to check for when doing inspections.

However,

Where the load is computed on a volt-amperes/square meter or square foot basis, the wiring system up to and including the branch-circuit panelboard(s) shall be provided to serve not less than the calculated load. This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s). Branch-circuit overcurrent devices and circuits shall only be required to be installed to serve the connected load.
If, in an effort to cut down on the number of AFCI breakers used, one circuit is serving significanly more area than other circuits, then a reasonable effort has not been made to comply with the principle of this section. I guess it is a judgement call as to what constitues significantly more area. Double the average? Triple? I'm not sure. The only reason I bring this up is that there seems to be a notion that you could put all of the bedrooms on one circuit, regardless of their area, and still be in compliance with the NEC. I think you could run into trouble with this section in doing that.

[ August 26, 2004, 11:29 AM: Message edited by: eprice ]
 
Re: bedroom circuits

I agree. For my part, I have not designed a residential building. But if I did, I would use the same type of spreadsheet panel schedule as a design tool. After I enter all the loads, and the KVA of each, the spreadsheet gives me the NEC load calculation, and tells me how nearly balanced the phase loads are. If I don?t like the balance, I will shift loads around until I do.

But we need to keep in mind the real-world fact that the day-to-day operation of the facility is beyond our control. When the owner turns this on, and that off, the phase balance changes.
 
Re: bedroom circuits

Read the comments and I may of missed somthing in the articles.....Im assuming this is residential Receptacle Outlets.

2002 nec....
Except as covered in 220.3(B)(10), receptacle outlets shall be computed at not less than 180 volt-amperes for each single or for each multiple receptacle on one yoke. A single piece of equipment consisting of a multiple receptacle comprised of four or more receptacles shall be computed at not less than 90 volt-amperes per receptacle.
This provision shall not be applicable to the receptacle outlets specified in 210.11(C)(1) and (2
 
Re: bedroom circuits

heco Welcome to the forum. :)

IMO, 220.3(B)(9) is not applcable to dwelling units, 220.3(B)(10) is the section we need to look at for dwelling unit outlets.

220.3(B)(10) Dwelling Occupancies. In one-family, two-family, and multifamily dwellings and in guest rooms of hotels and motels, the outlets specified in (1), (2), and (3) are included in the general lighting load calculations of 220.3(A). No additional load calculations shall be required for such outlets.

(1)All general-use receptacle outlets of 20-ampere rating or less, including receptacles connected to the circuits in 210.11(C)(3)

(2)The receptacle outlets specified in 210.52(E) and (G)

(3)The lighting outlets specified in 210.70(A) and (B)

[ September 22, 2004, 04:21 AM: Message edited by: iwire ]
 
Re: bedroom circuits

I agree with iwire. The opening few words of 220,3(B)(9), "Except as covered in 220.3(B)(10)..." exclude it from being applied to the outlets in dwelling occupancies covered in 220.3(B)(10)
 