This is a installation of ours that has been called into question by AHJ. I can not see the code violation may be I'm missing something.
This is a New SFD with (4) Bedrooms.
All outlets in B/R #2 and B/R #3 are supplied with (1) 15A AFCI protected circuit and do not serve any other outlets (total sqft of both B/Rs=338sqft) No problem here.
All outlets in B/R #4 are supplied with (1) 15A AFCI protected circuit and do not serve any other outlets (total sqft B/R #4=225sqft) No problem here.
All outlets in the Master B/R are supplied with (1) 15A AFCI protected circuit and also supply Here's the problem.
(5) Christmas/Holiday switched receptacle outlets located on the interior of the house under (5) windows on the front side of the house. (These recpt outlets are for the Christmas candles folks put in the windows at Christmas with a single pole switch for turning all (5)of these recpt outlets on and off without having to go around plugging and unplugging all the candles daliy) (1) of these recpt outlets is located under a window in the dining room. (this recpt is in addition to the ones required by 210.52 as well another 15A branch circuit feeding the lighting outlets in that room) This should apply:
The AHJ says you must add the sqft of each room that contains one of these "Christmas Outlets" into the 3VA used in the Master B/R. Thus saying when adding the sqft of the Dining Room and Study and B/R #3 you would be well over 600sqft or 1800VA per sqft for a 15A ckt. He stated that in order to "meet code" the "Christmas Outlets" would need to be on a dedicated 15A AFCI circuit with GFCI protection on the outlets requiring GFCI protection. He gave no code references.
My thought is that as long as you have the required outlets 210.52 requires as well as the lighting outlets required by 210.70 and are only putting in addition to these outlets the "Christmas Outlets" under windows for candles. Then I have not found the code reference that would not allow you from putting a "Christmas Outlet" supplied from the Master B/R under every window in the house.(as along as they are in addition to thoose required by 210.52 and meet any other special requirements)
Sorry for the long post. Just trying to get all the detail the 1st time.
This is a New SFD with (4) Bedrooms.
All outlets in B/R #2 and B/R #3 are supplied with (1) 15A AFCI protected circuit and do not serve any other outlets (total sqft of both B/Rs=338sqft) No problem here.
All outlets in B/R #4 are supplied with (1) 15A AFCI protected circuit and do not serve any other outlets (total sqft B/R #4=225sqft) No problem here.
All outlets in the Master B/R are supplied with (1) 15A AFCI protected circuit and also supply Here's the problem.
(5) Christmas/Holiday switched receptacle outlets located on the interior of the house under (5) windows on the front side of the house. (These recpt outlets are for the Christmas candles folks put in the windows at Christmas with a single pole switch for turning all (5)of these recpt outlets on and off without having to go around plugging and unplugging all the candles daliy) (1) of these recpt outlets is located under a window in the dining room. (this recpt is in addition to the ones required by 210.52 as well another 15A branch circuit feeding the lighting outlets in that room) This should apply:
Another (1) of these recpt outlets is located under a window in the study. (this recpt is in addition to the ones required by 210.52 as well another 15A branch circuit feeding the lighting outlets in that room)Another (1) of these recpt outlets is located under a window in the garage. (this recpt is in addition to the one required by 210.52 and is a GFCI recpt per 210.8(A)(2) as well another 15A branch circuit feeding the lighting outlets in the garage)Another (1) of these recpt outlets is located under a window in the Master B/R. The another (1) of these recpt outlets is located under a window in B/R #3. (this recpt is in addition to the ones required by 210.52)(total sqft of Master B/R=308sqft)210.52(B)(1)Exception No.1 In addition to the required receptacles specified by 210.52, switched recptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permited.
The AHJ says you must add the sqft of each room that contains one of these "Christmas Outlets" into the 3VA used in the Master B/R. Thus saying when adding the sqft of the Dining Room and Study and B/R #3 you would be well over 600sqft or 1800VA per sqft for a 15A ckt. He stated that in order to "meet code" the "Christmas Outlets" would need to be on a dedicated 15A AFCI circuit with GFCI protection on the outlets requiring GFCI protection. He gave no code references.
My thought is that as long as you have the required outlets 210.52 requires as well as the lighting outlets required by 210.70 and are only putting in addition to these outlets the "Christmas Outlets" under windows for candles. Then I have not found the code reference that would not allow you from putting a "Christmas Outlet" supplied from the Master B/R under every window in the house.(as along as they are in addition to thoose required by 210.52 and meet any other special requirements)
Sorry for the long post. Just trying to get all the detail the 1st time.