ptonsparky
Tom
- Occupation
- EC - retired
Loose connections can cause arcing..why cant loose bus bar and chair lugs contacts (with only few contact points)?
That probably started as a glowing connection. No spark.
Loose connections can cause arcing..why cant loose bus bar and chair lugs contacts (with only few contact points)?
High resistance for the amount of current is the key. In that video clip, weak contact ultimately caused heating and made things worse, as Tom mentioned initially it probably was just increased heat at the connection, eventually things got worse to create what is there now. Same can happen with the chair lugs. If not sufficient contact surface for the current being drawn, heating will occur and that heating will eventually cause more deterioration of the connection.Loose connections can cause arcing..why cant loose bus bar and chair lugs contacts (with only few contact points)?
Look closely...looks like aluminum wiring. Suppose the device was rated for Al? Torqued?High resistance for the amount of current is the key. In that video clip, weak contact ultimately caused heating and made things worse, as Tom mentioned initially it probably was just increased heat at the connection, eventually things got worse to create what is there now. Same can happen with the chair lugs. If not sufficient contact surface for the current being drawn, heating will occur and that heating will eventually cause more deterioration of the connection.
Maybe, EGC looks too small to be 12 AWG to me though. Aluminum isn't supposed to be smaller than 12 AWG, don't know if there was any out there anyway or not.Look closely...looks like aluminum wiring. Suppose the device was rated for Al? Torqued?
I know, I’m just twisting the knife.:huh:.
High resistance for the amount of current is the key. In that video clip, weak contact ultimately caused heating and made things worse, as Tom mentioned initially it probably was just increased heat at the connection, eventually things got worse to create what is there now. Same can happen with the chair lugs. If not sufficient contact surface for the current being drawn, heating will occur and that heating will eventually cause more deterioration of the connection.
I'm Googling about instances where new connections were done temporary and the arcing (without oxidation) is enough to suddenly melt the wire nuts without even any oxidation forming?
For Europeans. How did you setup your whole house AFCI protection?
Ok. So arcing by itself is not harmful. It can only cause harm if there is oxidation and resistive heating that can ignite the surrounding of the box, etc.
The arc spark is not enough to heat the surrounding and cause fire, right?
Anyway. For Europeans. How did you setup your whole house AFCI protection? In the US, AFCI breaker is only mostly 15A and it's mostly outlets too. There is no 60A breaker version, so it's more difficult to setup a whole house AFCI protection.
For the Americans. So you have two outlets in series. One a GFCI outlet and an AFCI outlet? So if you don't use AFCI breaker, you install an AFCI outlet, and connect another GFCI outlet in series to it? Better would be combined AFCI/GFCI outlet.
For the rest of the world with 240v electricity. Please share how you setup a whole house AFCI protection.
We're supposed to tourqe everything to manufacturers spec's , an old issue recently brought to the forefront of the NEC>>>>
110.14....
The truth being that the larger equipment is usually addressed before smaller terminations.
Our (at least my turf) AHJ's normally ask to see toolage, and leave it at that....
As an aside to this, much larger equipment instructs an annual retourqe , wich is seldom (if ever) done...
~RJ~
I'd like to inquire about using Torque screw drivers in breakers and panels. I read that:
https://www.ecmweb.com/contractor/do-you-have-calibrated-arm
"Torque screwdrivers are available, but very few electricians use them. Electricians indicated they were more likely to use a torque wrench on larger conductors, such as those found on
transformers or switchboards, but not on branch circuit connections. Only 36 of the 402 participants indicated they always use a torque wrench or screwdriver to make electrical connections, while 247 answered they sometimes use a torque wrench or screwdriver to make electrical connections."
Is it really true few electricians use them? In my country. I inquired all stores. They only have torque wrench for car wheels. No one carried any torque screwdrivers and no one use it.
But in my Siemens main panel with all GFCI breakers. I saw this:
In the main breaker. I saw the torque is 55 lb-in. In the individual breakers. It's 20 lb-in for AWG 10, also same for the Schneider Din rail breakers.
I plan to purchase a unit or sample to see how strong is 55 lb-in or 20 lb-in. Torque screwdrivers are selling in amazon for $200. May I know what is the best brand and model available there. It's a one time purchase only so need to make it right first and last time. I will also empower my electricians to use it all existing installations and recalibration to exact manufacturer's torques specifications.
Thats a step. The Klein screwdriver I purchased 20 years or so ago had a wide range of settings. A different brand newer driver require the purchase of two to get the ranges we commonly encounter.
My nephew works and teaches at a nuclear power plant. They test the torque settings of each tool before it is checked out of the tool crib. Each and every time.
My nephew works and teaches at a nuclear power plant. They test the torque settings of each tool before it is checked out of the tool crib. Each and every time.
That receptacle pictured still depends on screw pressure on the clamp to make a secure connection, it is not one where you just push conductor into back of receptacle and the connection is done.One of our ahj's ran w/that issue.....because we all stampeeded out and bought torque toolage >>>
https://www.homedepot.com/p/Capri-T...PIPHorizontal2_rr-_-204772217-_-206981635-_-N
meant little if they owner did not follow the certification ,usually indicating annual recalbration
a few local sparks found that there were little to few authorized entities available , and that the expense(s) involved resluted in a new purchase looking the economical route.
I can't fault my ahj , but i can say it's another good intent paving the road to perdition
As an aside , i found that installing the specified tourqe left me wanting to tighten things more than required. Apparently i had unwittingly overtouqued most installs as routine. So i have to ask, how have i harmed those many decades or work doing so? The spectre of liability robbing many an EC from a good nights sleep....:?
Further, there exists on the electrical market today many speed related electrical goods employing quick connect , or tool-less connections.
from devices....
lighting (recessed can JB)....
connectables.....
SQ D ,in the past also manufatured a 'backstab' style ocpd.
So it occurs to me that, i could wire the lions share of any given job w/o having to touque anything due to these products
~RJ~
Any connection has a higher possibility of failure if not used properly.Remember we have AFCI (Arc Fault Circuit Interrupter) precisely to avoid arc related fires. So arc forms when there is not sufficient wiring area for the current and there is a gap?
Also do you trust plastic screw nuts? Here in youtube I saw there is this loose wiring inside the wire nuts and even though AWG 14 can take the current with the 15A outlet. It burns due to the arc alone forming?