B bill001ma Member Dec 15, 2006 #1 What Is The Rating For 4 Awg Belding Cable Going Thru Seal-tite Or Raceway.(15 Feet). This Is For 460/3 60 In-line Voltage. I Have A Chart That Said It Is Rated For 100 Amps.(open Air).what Percentage Do I Use. Bill
What Is The Rating For 4 Awg Belding Cable Going Thru Seal-tite Or Raceway.(15 Feet). This Is For 460/3 60 In-line Voltage. I Have A Chart That Said It Is Rated For 100 Amps.(open Air).what Percentage Do I Use. Bill
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Dec 15, 2006 #2 Okay, I give up. What the heck is "Belding Cable"?
e57 Senior Member Location San Francisco, CA Dec 16, 2006 #4 Belden cable??? http://www.belden.com/ Anyway, gonna need more info than that like insulation type that you find on chart 310.16.... Last edited: Dec 16, 2006
Belden cable??? http://www.belden.com/ Anyway, gonna need more info than that like insulation type that you find on chart 310.16....
Rockyd Senior Member Location Nevada Occupation Retired after 40 years as an electrician. Dec 16, 2006 #6 Neoprene is not enough. The cable should be marked every two feet (400.6) Need that to properly identify it, so that it can be referenced to NEC. Thinking it might be in table 400.4
Neoprene is not enough. The cable should be marked every two feet (400.6) Need that to properly identify it, so that it can be referenced to NEC. Thinking it might be in table 400.4