Is the interior of a weaterproof box considered a wet or damp location when used outdoors?
Interestingly enough, the NEC appears to say that it is not, if properly sealed, while saying that the interior of a conduit outdoors is.Is the interior of a weaterproof box considered a wet or damp location when used outdoors?
Interestingly enough, the NEC appears to say that it is not, if properly sealed, while saying that the interior of a conduit outdoors is.
Almost every residential outdoor panel in existence would be in violation otherwise, and as we all know, if it's been done, it's legal. :wink:
Article 300.9 Nec 2008 for raceway. I don't know of an article that Larry's talking of.larry whats the code reference?
I have none.larry whats the code reference?
That's what I was referring to in the second sentence, about every outdoor panel.I also will go so far as to suggest that it is a violation to run NM in an outdoor panel. If we look at the definition of location wet and read art. 310.8(C) I cannot see it any other way.
I have none.
But, are water-proof wirenuts required for joints made in such boxes?
I already do both, but I always drill two 1/8" holes.Just turn the wire nuts up so the water can't get inside to the connection.
And drill an 1/8" hole in the bottom of the box so water can drain.:wink:
UL listing and the instructions on a bag of common tan twister wirenuts specify "dry locations only".NEMA said:Type 3R Enclosures constructed for either indoor or outdoor use to provide a degree
of protection to personnel against access to hazardous parts; to provide a degree of
protection of the equipment inside the enclosure against ingress of solid foreign objects
(falling dirt); to provide a degree of protection with respect to harmful effects on the
equipment due to the ingress of water (rain, sleet, snow); and that will be undamaged
This seems to imply they look at a location as where you are not what is in the box.ideal said:WeatherProof™ Applications
• exterior area and security lighting • outdoor signage
• outdoor power outlets • basement, garage, and car-port
• decorative patio & deck lighting circuits
• marine shore-power and dock • bathroom/spa vent fans
lighting • automatic carwashes
• traffic-signal control circuits • industrial hosedown/washdown
I also will go so far as to suggest that it is a violation to run NM in an outdoor panel. If we look at the definition of location wet and read art. 310.8(C) I cannot see it any other way.
Dont think i'm loosing any sleep on that one.![]()