Bending Grounding Electrode for a test well, 250.53(G)

Status
Not open for further replies.

MrJLH

Senior Member
Location
CO
An issue came up today at site where we cant install ground rods vertically due to rock and other under ground obstructions.

Seems the only solution is to install the ground rods horizontally 30" deep.

My question is does the code allow the ground rods to be "bent" by 90 degrees so that they can fit into the test well via bottom entry?

The length of the rods will still have 8ft of horizontal contact to earth.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No an 8' rod needs to be buried horizontal. IMO you could bend a 10' rod and still have 8' of it horizontal.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
No an 8' rod needs to be buried horizontal. IMO you could bend a 10' rod and still have 8' of it horizontal.

How will the electrons know about the bend in the rod? Why would it possibly matter? The rod is, after all, in contact with the earth along its entire length regardless of orientation to the ground's surface.



SceneryDriver
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How will the electrons know about the bend in the rod? Why would it possibly matter? The rod is, after all, in contact with the earth along its entire length regardless of orientation to the ground's surface.



SceneryDriver

The NEC says that the rod can be driven at up to a 45 degree angle or buried horizontally. If it's buried it has to be flat. In practical terms it probably makes no difference because I'm guessing that the electrons don't care. :)
 

MrJLH

Senior Member
Location
CO
How will the electrons know about the bend in the rod? Why would it possibly matter? The rod is, after all, in contact with the earth along its entire length regardless of orientation to the ground's surface.

SceneryDriver

It was just a thought that crossed my mind. Guess there is always a first time for everything.
 

kwired

Electron manager
Location
NE Nebraska
If you bend the rod into an L shape the sphere of influence of one side of the L will overlap the sphere of influence of the other side possibly leaving you with higher overall resistance to earth than if it were straight and in the same soil conditions.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If you bend the rod into an L shape the sphere of influence of one side of the L will overlap the sphere of influence of the other side possibly leaving you with higher overall resistance to earth than if it were straight and in the same soil conditions.
But 8' horizontal with a 2' stub-up wouldn't be any worse than 8' horizontal alone, right?
 