The Ground wire is the most safest wire in the electrical trade.
Chicar,
Originally, that was part of the idea of an EGC system.
Now that we have GFCI devices,
I suggest that the GFCI is safer than the EGC
because
(1) the GFCI trips at 5 milli Amp leakage,
whereas
(2) the OCPD/EGC trips at 20 Amps over an inverse-time period.
These figures are for illustration only, not from any table.
The 20 Amp OCPD is generally an Inverse-Time sensitive device.
The effect is that a 30 Amp load might trip in 30 seconds,
and a 100 Amp (fault) might trip in 1/2 second.
The GFCI will trip immediately at 5 milli Amps (4-7 mA range).
A human connected in the path of a ground-fault could sustain irreparable damage before a regular EGC system functions during a 1/2 second.
These figures are for illustration only, not from any table.
You probably already know these things. Le entiendes.
Sorry for belaboring the point