I change several 3/ to 2/prong yesterday to bring house up to code--nothing hooked to green screw on the ones I took out.
Ready,
Could you have labeled them "Not Grounded" ?
I change several 3/ to 2/prong yesterday to bring house up to code--nothing hooked to green screw on the ones I took out.
Why do you need all the receptacles to have a ground ? Other than for a few items it is not even used. Nothing unsafe about no ground for things that have 2 prong plugs
I didn't think so but could I? Remember that the receptacles I changed back to 2/prong were not GFCI protected.Ready,
Could you have labeled them "Not Grounded" ?
The GFCI is also an inverse time device. The UL standard will permit a 5.8 second time to trip for a 5 mA fault. Most will trip a lot quicker than this, but that time is permitted by the standard....
The GFCI will trip immediately at 5 milli Amps (4-7 mA range).
...
that's what I thought. thanks.Not and be code compliant.
Roger