Went on a site visit to an industrial plant the other day and saw a configuration like this:
600A fused disc.---2 sets 350MCM---600A disc. w/175A fuses---150KVA xfrmer---3/0---600A main breaker panel. There's a second tap on the transformer with another set of 3/0 and a second 600A main breaker panel. The 175A fuses would protect the secondary windings of the transformer, but the secondary tap conductors are not protected by the 600A main breakers. Would the least expensive way to fix this be to replace the secondary conductors with 2 sets of 350MCM (600A wire)? This appears to meet 240.21(C)(2) or (3). (Secondary conductors are less than 25' and may be less than 10').
600A fused disc.---2 sets 350MCM---600A disc. w/175A fuses---150KVA xfrmer---3/0---600A main breaker panel. There's a second tap on the transformer with another set of 3/0 and a second 600A main breaker panel. The 175A fuses would protect the secondary windings of the transformer, but the secondary tap conductors are not protected by the 600A main breakers. Would the least expensive way to fix this be to replace the secondary conductors with 2 sets of 350MCM (600A wire)? This appears to meet 240.21(C)(2) or (3). (Secondary conductors are less than 25' and may be less than 10').