Re: Best way to get "Clean" power to a computer ou
I get tickled when I see post like this one. There are a lot of myths and misconceptions about power quality. There is no such thing as clean reliable power from a utility company. There is not a one utility that will guarantee their service, and for good reason, it is not possible.
Many believe by using an IGR all their problems will go away only to find out it did nothing or made the problem worse. Others will think to add a TVSS device at the equipment and expect miracles, only to be disappointed. While others will go down and buy a cheap UPS and expect problems to go away, only to learn later the only thing it protected against was a 5-minute outage and still has noise problems.
There is no magic system that is going to provide you with clean uninterruptible power. It takes a combination of systems with proper design to give you clean power up to without interruption 99.9% of the time.
A UPS can go a long way if the proper unit is selected. The problem is the type you would choose. The inexpensive ones are what is called a standby UPS. These units have a small battery charger, battery, inverter, and some sort of switching mechanism. Under normal operating conditions the equipment is connected to commercial line power and waits in “stand-by”. In the event the power fails for a prescribed number of cycles it switches to battery-inverter. They offer no power line conditioning. These types of units are what you find in residents and small businesses connected to a PC. They range in size from 200 VA up to 1200 VA.
The next step up is called “stand-by interactive” UPS. It is similar to the above unit except the inverter is on line and connected to a ferroresonant transformer with a static bypass switch. During normal operation the equipment is connected to commercial AC power like above, but the inverter does provide some voltage regulation in a boost and buck manner. Again if a failure of power occurs the battery-inverter take over. These units are also available in sizes popular for residential from 200 VA up to a few KVA. Some data processing departments will use these type in a rack mounted model to save money and cut corners.
The next step up is the “double conversion” UPS units used by company’s and people who care about PQ. A double conversion UPS input power is first converted to DC. The DC is used to charge batteries and to constantly operate the inverter at full load. The load is completely isolated from the input. There are lots of extras that can be optioned like a ferroresonant output isolation transformer for further power line conditioners, static bypass for maintenance, parallel redundant modules for extra protection in the event the primary rectifier or inverter fails. These units range in size from 2KVA up to 750 KVA The larger unit will use PDU’s for distribution. A PDU is a step-down/isolation transformer with power line conditioning and alarms.
But even a quality UPS will not carry through a long-term outage. For that you need a generator. Oh well I will quit rambling on, sorry to preach.