Nice curves. I'm all for nice curves.bearings and balance
But starting has to take account of inertia of the fan rotor.
Nice curves. I'm all for nice curves.bearings and balance
Nice curves. I'm all for nice curves.
But starting has to take account of inertia of the fan rotor.
Not in my experience.that is why the fan design engineer selects a matched motor
a fan is low interia
Not in my experience.
We did a few variable speed fan drives in cement works in the 3,000 HP range. Low inertia they were not.
But what do I know.
OK.this is 50 hp
we know this motor starts
so lr torque is sufficient to overcome wk^2
the issue is mechanical, the bearings
they loosened the belts to take force off the bearings
now they squeal
it will require the same torque regardless of starter type to get it spinning
the issue is not the motor stalling due to inertia/mismatched load
we are losing sight of the issue
reduced torque may mask the problem but won't help the root issue
they are burning the belts via slipping
This isn't an electrical problem; it's a ID-ten-T problem, and a soft starter isn't likely to solve it. Installing a soft starter might eliminate the squeal during start, but with the belts this loose, they will slip a lot and their life will be short. I would encourage the customer to identify & solve the fundamental problem, not a secondary problem caused by Appalachian Engineerin'.
These two posts actually address some very important points.does it start with dampers open or closed?
I've used that exact same demo, and yes, I've had to convince more than a few Civil PEs of this.You might show the venerable PE how a vacuum cleaner motor speeds up when you block the air flow. I find it a very a very convincing demonstration.
Sent from my XT1585 using Tapatalk
You might show the venerable PE how a vacuum cleaner motor speeds up when you block the air flow. I find it a very a very convincing demonstration.
Sent from my XT1585 using Tapatalk
Incorrect.this is 50 hp
we know this motor starts
so lr torque is sufficient to overcome wk^2
the issue is mechanical, the bearings
they loosened the belts to take force off the bearings
now they squeal
it will require the same torque regardless of starter type to get it spinning
wrongIncorrect.
Lower torque will just take longer to get to the same speed.
Installing a VFD and modulating blower speed while in operation - probably not a good idea. Just ramping the thing up to speed when starting vs, giving it "full york" can have advantages. The burner likely goes through a purge cycle before ignition, purge cycle probably doesn't start until a pressure switch proves there is sufficient air flow - so what if it takes 10-15 seconds to start vs 5? Purge cycle won't start until there is pressure either way.I would not do this without something in writing from boiler manufacturer, boiler inspector, and insurance agent. Modifying boilers is a big no-no.
I had pretty much exact problem you are describing maybe about 10-15 years ago on a boiler for one of my regular clients. It only driven by a 15 hp motor, but same thing, tighten belts so they don't slip when starting and then they end up replacing bearings pretty frequently. This blower runs at same speed or possibly even a little faster then the motor, so and with it's mass doesn't accelerate in an instant. Decided to try soft starter on it, had pretty noticeable results in maintenance issues right away, not going through so many belts or bearings.They are having trouble with the fan bearings and want to be able to loosen the belts to keep some of the pre load off the bearings. With the belt loosened to lower the load on bearings the squalls really loud and burns up the belts. The boiler technician is the one that wants the belts looser to prolong bearings.
My application was a steam boiler. Depending on steam load, it may only start once an hour, maybe even two hours when plant isn't in operation and not heating season, but on higher demand may start 4 or 5 times an hour.if you do not plan on controlling speed a vfd is overkill
a ss should do it
I assume lt runs continuously? or is it cycled?
Or lack of inertia. No motion at all I guess is still inertia - just on the opposite end of the spectrum of when running at normal speed, or the middle of the spectrum for something that can operate in reverse direction.Nice curves. I'm all for nice curves.
But starting has to take account of inertia of the fan rotor.
Boiler possibly could have had better design, but I wasn't going to redesign it. Something other then belt drive likely would have been better. Working with what I had, soft start seemed to be the best balance of how to handle this.this is 50 hp
we know this motor starts
so lr torque is sufficient to overcome wk^2
the issue is mechanical, the bearings
they loosened the belts to take force off the bearings
now they squeal
it will require the same torque regardless of starter type to get it spinning
the issue is not the motor stalling due to inertia/mismatched load
we are losing sight of the issue
reduced torque may mask the problem but won't help the root issue
they are burning the belts via slipping
Exactly what happens in my application, takes longer to get to speed but works just the same once it gets there, plus we don't go through so many belts or bearings anymore. Only thing I did wrong first time was not put in a big enough soft starter. Yes it was good for 15 HP, but not really for a higher inertial load or as many starts per hour as we sometimes get. When first one failed researched a little more and figured I probably needed a larger one in the first place so replaced with a larger one, and have been going well for some time now.Incorrect.
Lower torque will just take longer to get to the same speed.