The wording in 240.21(C) makes clear than one can have multiple sets of conductors coming off a transformer secondary. The application at hand is an outdoor customer owned pad mounted transformer so 240.21(C)4 applies.
The secondary is 480V so FLA times 1.25 is 338Amps. Next size up per 240.6 is 350Amp.
But I'm going to have two secondary breakers each equal in size. So that's easy. two 175A-3P OCPD's.
So a) anything wrong with the above and b) what if they were different sizes. Is that permissible? And if so, where is this made clear in the NEC? Or is it simply silent on the matter?