Big Ass Fan

Status
Not open for further replies.

eds

Senior Member
Installing a Big Ass Fan (14' Essence Model), mounting support will be above finished ceiling. Power cable exits the top of the down rod and will enter a 4 square box in ceiling. Power cable seems to be a type of so chord, is this rated to be concealed above the ceiling?
 
Power cable won’t be in conduit to j-box unless I sleeve it from down rod to j-box
 
Installing a Big Ass Fan (14' Essence Model), mounting support will be above finished ceiling. Power cable exits the top of the down rod and will enter a 4 square box in ceiling. Power cable seems to be a type of so chord, is this rated to be concealed above the ceiling?
Is there any listing information on the cord?
 
Finished ceiling? What type of ceiling?
 
Metal for the ceiling, hard wired, specs out a 10 amp breaker. Didn’t get a picture of the chord tonight, hopefully tomorrow.
 
Is it a factory assembly? The last one I put up was completely prewired, and plugged right into a 15r.
Yes factory, molex plug from the fan, molex plug on the factory whip that feeds down the down rod. Individual conductors on the other end of the whip.
 
So, SO cord (capped or hard wired), "buried" above a finished ceiling ?? I would say NEC is a no on that?
 