I have a situation that happened recently and i am wondering if someone can tell me what actually occured electrically under these circumstances.
A shutdown was planned but was not thouroughly investigated and some 277V panels that needed to be kept energized had to have temporary power in a hurry.
The contracted electricians grabbed a 3 phase breaker from a 277/480 panel that appeared to have a nuetral. We found out later that someone had run a nuetral to the nuetral bar but it was never terminated any where in the main distribution. there was a ground, but this too only went as far as the first junction box, so technically the conduit was the only ground.
The only reason it had not been caught before hand is the only thing being supplied by this panel are transformers for other sub panels. Of course the transformers are grounded to building steel.
As a result we lost a bunch of power paks for lighting sensors. They actually were melted in the center. We lost about 15 exit lights, all led, 277V. Now 6 months later we have a bunch of ballasts that are failing. :roll:
A shutdown was planned but was not thouroughly investigated and some 277V panels that needed to be kept energized had to have temporary power in a hurry.
The contracted electricians grabbed a 3 phase breaker from a 277/480 panel that appeared to have a nuetral. We found out later that someone had run a nuetral to the nuetral bar but it was never terminated any where in the main distribution. there was a ground, but this too only went as far as the first junction box, so technically the conduit was the only ground.
The only reason it had not been caught before hand is the only thing being supplied by this panel are transformers for other sub panels. Of course the transformers are grounded to building steel.
As a result we lost a bunch of power paks for lighting sensors. They actually were melted in the center. We lost about 15 exit lights, all led, 277V. Now 6 months later we have a bunch of ballasts that are failing. :roll: