Table310.15(B)(6) lists residential service sizes up to 400amps. If you're installing a residential service that's larger than 400amps, can you use Table310.15(B)(6) or are you forced over to the lower amperage allowances of Table310.16 ?
I was inspecting a service trench that had parallel 350 Al conductors in para 3" PVCs. Services over 400amps require CTs, so the electricians plan was to bring the para 350s into the CT cabinet and then use the multiple load lugs to come out of the cabinet 3 times to 3 different 200amp main panels in the basement.
If you take the ampacity for the Al 350s from Table310.15(B)(6), you get 300x2, which gives you the needed 600amps for the three 200amp mains. But if you're forced to use Table310.16, Al 350s can be used for 250amps on 75?C CT lugs [250x2=500amps] or 280amps on 90?C CT lugs [280x2=560amps], which falls short of the needed 600amps for the three 200amp mains.
So what do you think ? I know what my conclusion was but I'd like to find out how others see it.
David
I was inspecting a service trench that had parallel 350 Al conductors in para 3" PVCs. Services over 400amps require CTs, so the electricians plan was to bring the para 350s into the CT cabinet and then use the multiple load lugs to come out of the cabinet 3 times to 3 different 200amp main panels in the basement.
If you take the ampacity for the Al 350s from Table310.15(B)(6), you get 300x2, which gives you the needed 600amps for the three 200amp mains. But if you're forced to use Table310.16, Al 350s can be used for 250amps on 75?C CT lugs [250x2=500amps] or 280amps on 90?C CT lugs [280x2=560amps], which falls short of the needed 600amps for the three 200amp mains.
So what do you think ? I know what my conclusion was but I'd like to find out how others see it.
David