mpd said:david
I am suprised to hear you say you NEVER get load calculations on residential, what they do without a permit is there problem, how do you enforce art 220?
load calcs. must be done at plan review to verify the service is adequate for the load, (new or existing). requiring load calcs. covers me as an inspector.
and if they make major changes to a house that increases the load, I require a new load calc, updated plans and permit. I have had architects design additions that are bigger than the house and have no clue what the existing service size or load is, IMO it is a must
The entire time I've worked as an inspector, I have yet to see someone try to put in a service of less than 150amps on even the smallest house. I've seen a 100amp fuse or damaged panel be replaced by a 100amp breaker panel, but that's it. Maybe it's just the common practice in this area of the country, but attempts at small services are just unheard of. Maybe this is the reason that we never look at calcs.
Most houses I inspect have 200amp services and a few have 400amp. Over 400amp is very very rare but I see a few. Under 150s are never seen at all.
Since the services we see are installed according to Table310.15(B)(6) and the actual load when every item in the whole house is on is about one quarter of the main breaker amperage, I can't see what we would accomplish by looking at residential calcs.
David