Hello there :
I am running a large bitcoin data center and wondering about the best way to achieve 240/1 voltage for computers.
I currently have 500 kva transformer that is 12470 delta primay 480/277 wye secondary. I purchased a new transformer for 2500 kva to accomodate higher power in the data center with the same voltages. But all of my computers PSUs are rated for 240 volts. I considered the following options to get 240 volts to the power supply units cost effectively and wondering if there are better options.
3. Use secondary transformer and 415/240
Pros: Ideal voltage
Cons: Not easy to find these European transformers and takes long time for getting replacement if one fails.
Using 416/240V is becoming more common for data center applications. The power supplies are designed to work 240V L-N. Why use a 2 pole breaker to supply 208V when a single pole can supply 240V?
-Jon
And the winner is! Finally, the right way to do it.
See http://forums.mikeholt.com/showthread.php?t=164464
That solution may be acceptable, provided the primary voltage does not exceed 10%. If it exceeds 10%, it may not be possible to bring secondary voltage down to within 10% of 240V for normal operation of PSU of OP as the transformer tapping already used at the rated primary voltage to bring down secondary voltage to within 10% of 240V.he already purchased a 2.5 mva 480/277 xfmr
he can easily get 420/240 out of it, possibly at no cost, or small cost amortized over several years
That solution may be acceptable, provided the primary voltage does not exceed 10%. If it exceeds 10%, it may not be possible to bring secondary voltage down to within 10% of 240V for normal operation of PSU of OP as the transformer tapping already used at the rated primary voltage to bring down secondary voltage to within 10% of 240V.
I thought the principal reason for using 240Y in American data centers was the energy savings made possible by NOT transforming the voltage a second time.
cannibis grow barns, and bitcoin mines.... welcome to americas
new industrial revoltion
Derivation of above (size of utility regulator-100MVA) please.he can have the utility supply a 100 MVA (0.125 x 2.5 mva/(sqrt3 x 13.2 kv) x 13.2 kv/sqrt3) voltage regulator
That is one reason, but the other main reasons are higher efficiency of server power supply operation and smaller conductors.I thought the principal reason for using 240Y in American data centers was the energy savings made possible by NOT transforming the voltage a second time.
Well cool, thanks for coming back and giving us an update. Just curious, do you take service at primary voltage? Seems like you have lots of control over the transformer, or a really laid back POCO.....Wow. The original poster resurrecting a 'zombie thread' to tell us what happened.
Regarding your background: this site has specific rules about service professionals in their work capacity. It doesn't matter what you know or if you can actually do what is being described; what matters is that you be functioning in your licensed professional capacity.
For example, if I ask a question about installing an outlet in my kitchen, I would be violating the rules since for _me_ that would be a DIY project. My professional relation to the electrical industry has nothing to do with residential electrical installation.
In your case, if you are working as a facilities manager, and a licensed electrician is doing the electrical work, then your questions are perfectly kosher in helping you plan the work you are having the electrician do. On the other hand, if _you_ are doing this work, then you are violating the forum rules because physician, physicist and programmer all suggest that you are competent and can handle _large_ DIY electrical jobs...but you are not suitably licensed.
Regarding the use of power supplies outside of their rated operating range, this almost certainly violates the electrical code. IMHO as long as you provide the necessary safeguards to ensure that failure of this hardware does not put people at risk, I personally think that this is a reasonable violation...but really that is between you, your investors, the AHJ, and your insurance company. I believe that if you are putting people (employees) at risk while cutting corners then this is morally and legally reprehensible. (What I mean by protecting people, for example: if you cut corners on code to build your server ensemble, but you don't let people enter the server room while it is powered, then the code violations are simply putting property at risk. But if you have employees walking the racks troubleshoot hardware _while it is on_ then code violations put those people at risk.)
Regarding your C13 and C14 outlets, you should get the actual datasheets. It is quite likely that the receptacle configuration is for 250V with a higher actual electrical rating. NEMA configuration plugs and receptacles are often manufactured with a 480V or 600V actual rating, but in configurations specific to 120 or 208 or 250V. In other words the layout of the pins is akin to a color code telling you what voltage that device is intended to supply or receive, but the actual voltage rating is higher.
-Jon
I am able to stay at my first option without any issue. This is what I did...
1. Installed the transformer with native settings of
12470/7200 Primary > 480/277 Secondary.
2. Changed the taps on the transformer to the lowest level and we got about 250-255 volts L-N setting.
3. I bought few PSUs that are rated for 200-265 volts. Tried them. They worked fine without any issues. Then we used the regular 240 rated PSUs, they worked fine as well. In-fact all of them are performing better as the amperage is lower at a bit higher voltage to get the desired wattage. With lower amperage, less heat and higher efficiency. Have been operating without any issues for the past 2 years.
You can review the benefits of 240 L-N and 277 L-N vs the 208 L-L configuration in this whitepaper.
Only concern I see with my set up is, C13 and C14 outlets are only rated for 250 Volts and not for 277 Volts. after tapping the voltage down, I am close to 250 anyway.