We will have another go at this Monday, but thought you fine folks would be interested. Got an ABB ACH550 that is being switched from hard wire to RS-485/Modbus control as part of a PLC upgrade. I've been doing the wiring while a gal is doing the programming, but we help each other out.
Soooo, comes commissioning time and we are trying to get the VFD to run with the help of tech support (This parameter, that parameter, the other parameter, nothing works, thanks for your help, good-bye...) RS-485 is working fine. The speed command on the keypad is changeable from the PLC when in "AUTO" on the keypad (while not changeable from the keypad) but won't start. However, when in "OFF" on the keypad, the PLC cannot change the speed command (while the keypad can), but can start the VFD!
In other words, when the PLC can change the speed command (in AUTO) it cannot start the VFD, and the keypad cannot start the VFD nor change the speed command. But when the PLC can start the VFD (in OFF) it cannot change the speed command, but the keypad can change the speed command (but not start the VFD.)
Not asking for advice at this point, just sharing a bizarre situation. I'm working on a spreadsheet app where I can enter the hexadecimal values of the Command Words and Status Words from the RS-485/Modbus comms as displayed on the keypad and see which bits are ON or OFF and what they control or indicate.
Soooo, comes commissioning time and we are trying to get the VFD to run with the help of tech support (This parameter, that parameter, the other parameter, nothing works, thanks for your help, good-bye...) RS-485 is working fine. The speed command on the keypad is changeable from the PLC when in "AUTO" on the keypad (while not changeable from the keypad) but won't start. However, when in "OFF" on the keypad, the PLC cannot change the speed command (while the keypad can), but can start the VFD!
In other words, when the PLC can change the speed command (in AUTO) it cannot start the VFD, and the keypad cannot start the VFD nor change the speed command. But when the PLC can start the VFD (in OFF) it cannot change the speed command, but the keypad can change the speed command (but not start the VFD.)
Not asking for advice at this point, just sharing a bizarre situation. I'm working on a spreadsheet app where I can enter the hexadecimal values of the Command Words and Status Words from the RS-485/Modbus comms as displayed on the keypad and see which bits are ON or OFF and what they control or indicate.