Got a service call today to a new residence that was finished in 2022.
As I’m there working I start noticing several things that stand out .
- Several 18 Cubic inch nail on boxes that have as many as 15 #14 conductors not counting EG’s and the device.
- AC cable on basement poured walls with one strap at the top plate and one 6” above the 4” square box. Just over 6’ of dangling cable. Top strap is a plastic NM staple in the bottom of the floor joist.
-As many as 5 14/2 NM cables in a 3/4” NM connector entering the panel.
- Two of the boxes I opened had the equipment grounds twisted with no wire nut or crimp securing them.
- #6 bare Cu GEC attached to the exposed rebar ufer with 3 clamps. (Why 3 ????) Min#4 required.
These things were in just the utility room.
I chuckled when I saw the Final inspection sticker.
Approved.
Inspectors signature was a scribble not even close to being legible.
It’s a shame that the homeowner is getting this type of work on a $400K plus home.
As I’m there working I start noticing several things that stand out .
- Several 18 Cubic inch nail on boxes that have as many as 15 #14 conductors not counting EG’s and the device.
- AC cable on basement poured walls with one strap at the top plate and one 6” above the 4” square box. Just over 6’ of dangling cable. Top strap is a plastic NM staple in the bottom of the floor joist.
-As many as 5 14/2 NM cables in a 3/4” NM connector entering the panel.
- Two of the boxes I opened had the equipment grounds twisted with no wire nut or crimp securing them.
- #6 bare Cu GEC attached to the exposed rebar ufer with 3 clamps. (Why 3 ????) Min#4 required.
These things were in just the utility room.
I chuckled when I saw the Final inspection sticker.
Approved.
Inspectors signature was a scribble not even close to being legible.
It’s a shame that the homeowner is getting this type of work on a $400K plus home.