- Location
- New Jersey
- Occupation
- Journeyman Electrician
I would expect any decent inspector to find the things on this list since they're so obvious.1- Several 18 Cubic inch nail on boxes that have as many as 15 #14 conductors not counting EG’s and the device.
2- AC cable on basement poured walls with one strap at the top plate and one 6” above the 4” square box. Just over 6’ of dangling cable. Top strap is a plastic NM staple in the bottom of the floor joist.
3-As many as 5 14/2 NM cables in a 3/4” NM connector entering the panel.
4- Two of the boxes I opened had the equipment grounds twisted with no wire nut or crimp securing them.
5- #6 bare Cu GEC attached to the exposed rebar ufer with 3 clamps. (Why 3 ????) Min#4 required.
1) A quick eyeball on the rough would find the overfilled box without even looking inside the box.
2) The cable should not be dangling and should be properly supported. Maybe the inspector thought it was MC cable which requires no more than 6' between supports.
3) This one should have been noticed in two seconds.
4) Another indication that they never looked inside the boxes.
5) Not sure why they used 3 clamps but that's not an issue. The #6 may or may not be an issue depending on the size of the service. The GEC for a 100 amp service can be as small as #8.