What is it about block heaters tripping gfci receptacles!?!
I've been called out more than once because a gfci was tripped by a block heater.
The call I got this evening was from a customer I've done a fair amount of work for that has a ranch with various outbuildings.
Last year i installed a receptacle outside an old garage that is mostly used for storage. I ran the circuit complete to a dedicated gfci. He said the gfci tripped after his tractor was plugged into it for about 10 minutes. I gave him "the talk" about how GFCI's work and maybe something is wrong with his block heater and that the gfci is doing what it was designed to do...
He said the block heater was brand new and doesn't have more than an hour on it yet. I told him I'd come out and take a look.
If the heating element was/is shorting out to ground (tripping the gfci)it must be taking a few minutes to happen according to the guy. I will ohm out to ground on the power cord, also probably ohm out ground to chassis.
Is this one of those situations where a megger would help out in testing the element.
Not totally sure why the heater took 10 minutes to trip the gfci?
Any suggestions for more ways to check out the block heater?
Of course I'll also check out the gfci and circuit as well.
Thanks!
I've been called out more than once because a gfci was tripped by a block heater.
The call I got this evening was from a customer I've done a fair amount of work for that has a ranch with various outbuildings.
Last year i installed a receptacle outside an old garage that is mostly used for storage. I ran the circuit complete to a dedicated gfci. He said the gfci tripped after his tractor was plugged into it for about 10 minutes. I gave him "the talk" about how GFCI's work and maybe something is wrong with his block heater and that the gfci is doing what it was designed to do...
He said the block heater was brand new and doesn't have more than an hour on it yet. I told him I'd come out and take a look.
If the heating element was/is shorting out to ground (tripping the gfci)it must be taking a few minutes to happen according to the guy. I will ohm out to ground on the power cord, also probably ohm out ground to chassis.
Is this one of those situations where a megger would help out in testing the element.
Not totally sure why the heater took 10 minutes to trip the gfci?
Any suggestions for more ways to check out the block heater?
Of course I'll also check out the gfci and circuit as well.
Thanks!