I have a blower motor that draws 49 amps on start up, and 11.2 amps running.
I am concerned about the supply conductors I installed which are No. 12 AWG.
What is the correct way to determine the supply conductor size?
Also this motor is thermally (internal) protected, is any other protection required other than the circuit breaker?
Motor spec's:
Phase: Single (1)
V 115/208-230
A 22/12.5-11.0
Duty: CONT.
max. amb. 40
SF 1.0
RPM 3450
code H/M
I am concerned about the supply conductors I installed which are No. 12 AWG.
What is the correct way to determine the supply conductor size?
Also this motor is thermally (internal) protected, is any other protection required other than the circuit breaker?