... Fan moving at 120% speed requires 173% ( (60Hz/50Hz)3 ) the amount of power from the motor. If we assume the fan needed 2.2kW at 50Hz, it will need 3.8kW at 60Hz, but the motor is only rated for 2.2kW. ... the root cause is the physics. ...
All of the above, plus:
- Hire a mechanical engineer to visit your site and conduct a formal analysis of whether it's reasonable to run this system at 120% of design speed.
- If the answer is yes, buy & install a 3.8 kW (5 Hp) 60-Hz motor. A 3-phase motor if you have 3-phase power available. Replace the motor starter with a larger one if need be.
- If the answer is no, buy & install a 5:6 ratio gearbox.
- If the answer is something else, implement whatever solution your maniacal engineer suggests.
- Bill your time, the engineer's time, and all the other costs of all this rigamarole to whichever sharp-pencil financial genius thought buying a 50-Hz Chinese machine would save money.