Hey guys need some help on this one.....
First off let me apologize to my late father and Mr. Cronkhite for the bad drawing.
I have a job with 2 rooftop condensers for a remote AC compressor. They are OVER 50 years old. I replaced 1 bad motor with a new one of comparable horsepower and did only the electrical repairs to get power from the "t" unilet to the motor (nothing else was in bad condition).
Today I get a call to go back to the job as our HVAC tech found a short on "C phase" I verified this, and went looking for it. I found a burned splice from the motor leads to the conductors back to the starter, causing a single phase condition at this motor only
So here is the question, seeing as both motors are fed from a common disconnect and starter, is it possible (and probable) that the failure at motor 2 caused a "domino effect" and thereby took out motor 1 ....... I am thinking the single phase condition blew the fuse, which created a "single phase" condition on the remaining moto, and this overheated the windings and caused them to short out.
I have attached a diagram of how things are currently wired.... I am thinking that either a second starter, disconnect, or both are needed to prevent this.
Any thoughts or ideas?????
Howard
First off let me apologize to my late father and Mr. Cronkhite for the bad drawing.
I have a job with 2 rooftop condensers for a remote AC compressor. They are OVER 50 years old. I replaced 1 bad motor with a new one of comparable horsepower and did only the electrical repairs to get power from the "t" unilet to the motor (nothing else was in bad condition).
Today I get a call to go back to the job as our HVAC tech found a short on "C phase" I verified this, and went looking for it. I found a burned splice from the motor leads to the conductors back to the starter, causing a single phase condition at this motor only
So here is the question, seeing as both motors are fed from a common disconnect and starter, is it possible (and probable) that the failure at motor 2 caused a "domino effect" and thereby took out motor 1 ....... I am thinking the single phase condition blew the fuse, which created a "single phase" condition on the remaining moto, and this overheated the windings and caused them to short out.
I have attached a diagram of how things are currently wired.... I am thinking that either a second starter, disconnect, or both are needed to prevent this.
Any thoughts or ideas?????