g-and-h_electric
- northern illinois
- supervising electrician
Hey guys need some help on this one.....
First off let me apologize to my late father and Mr. Cronkhite for the bad drawing.
I have a job with 2 rooftop condensers for a remote AC compressor. They are OVER 50 years old. I replaced 1 bad motor with a new one of comparable horsepower and did only the electrical repairs to get power from the "t" unilet to the motor (nothing else was in bad condition).
Today I get a call to go back to the job as our HVAC tech found a short on "C phase" I verified this, and went looking for it. I found a burned splice from the motor leads to the conductors back to the starter, causing a single phase condition at this motor only
So here is the question, seeing as both motors are fed from a common disconnect and starter, is it possible (and probable) that the failure at motor 2 caused a "domino effect" and thereby took out motor 1 ....... I am thinking the single phase condition blew the fuse, which created a "single phase" condition on the remaining moto, and this overheated the windings and caused them to short out.
I have attached a diagram of how things are currently wired.... I am thinking that either a second starter, disconnect, or both are needed to prevent this.
Any thoughts or ideas?????
Howard
Howard