Is this equipment UL aproved
Is this equipment UL aproved
Sorry I had to open that can of worms.
Is this equipment UL aproved
Sorry I had to open that can of worms.
From that same sheet:pbeasley said:The Atomic 3000 unit is an auto-ranging electronic power supply, you can find the cut sheet at http://www.martin.com/marketing/files/Atomic_col_deto_broch_low.pdf
Well, I stand corrected. Thanks all.Rampage_Rick said:If all else fails, RTFM... Check out pages 6 and 7. (color code on pg 7)
http://www.lysudlejning.dk/images/Manual/UM_Atomic3000_EN_C.pdf
The auto-ranging power supply automatically adjusts to any 50 - 60 Hz AC power supply from 90 to 260 volts. No adjustment is necessary.
The current required by the Atomic 3000 varies according to lamp type, power mode, and usage. To avoid overload, allow one 16 or 20 amp branch circuit per fixture to operate the MAX-15 model at full power. Two fixtures may be placed on a 16 amp branch circuit if they are operated in low power mode or use the MAX-7 lamp.
Use 2.5 mm2 (13 AWG) or larger power feed cables and keep runs as short as possible.
The club owns these. These are only 2 units out of 28 Martin units. I'm supplying the cord bodies and recepticles, so thats not an issue.dbuckley said:So it's an Atomic we're dealing with.
An Atomic wants to be fed with the highest voltage available, to get maximum output. Thus in the USA 208V with the MAX-15 lamp is what most folks using Atomics choose to use, as they get power from a distro fed with 208Y/120.
Voltage is important for these sorts of strobes, as the strobe tube is wired directly across the mains, and thus more volts == more brightness. You don't buy an Atomic unless you are looking for a lot of brightness.
There is one other issue I'll amplify; It's mentioned in the manual - take enormous note of the number of Atomics you can have per circuit. Atomics can and do pop breakers, so a strobe per circuit is about the limit.
Using two hots of a 208Y to feed an appliance that expects a neutral is an interesting diversion; I don't know but I guess that the US rental houses just put a 4 wire NEMA plug on and wire the brown and blue to the two hots. I'd recommend that you ring a local lighting or production house and ask what plugs their 208V Atomics have...