flengineer
Member
- Location
- Miami, FL
The main service entrance for a school comes into the Main Switchgear Room where it is grounded to two ground rods, foundation steel and the cold water pipe. The main switchboards feed satellite electrical rooms in four other buildings. At each satellite room, there is a ground bus tied to two ground rods, foundation steel and cwp. The feeder's EGC from the switchgear room is also bonded to this ground bus.
The school was opened for a year with no visible problems. When the school reopened after the summer, the water was visibly blue in several locations.
Testing revealed high concentrations of copper in the water. Electrolysis caused by a grounding problem is being blamed for the blue water.
The campus has two water services, one serving four buildings and another serving one building. The water pipe outside the building is ductile iron pipe (supposedly not electrically continuous) except for the last 20' at each service entering the building which is copper. Piping within the building is copper. The water from both water services has elevated copper levels.
Any thoughts on how to verify that this is a grounding problem and isolate the problem?
The school was opened for a year with no visible problems. When the school reopened after the summer, the water was visibly blue in several locations.
Testing revealed high concentrations of copper in the water. Electrolysis caused by a grounding problem is being blamed for the blue water.
The campus has two water services, one serving four buildings and another serving one building. The water pipe outside the building is ductile iron pipe (supposedly not electrically continuous) except for the last 20' at each service entering the building which is copper. Piping within the building is copper. The water from both water services has elevated copper levels.
Any thoughts on how to verify that this is a grounding problem and isolate the problem?