jb3551
- Dahlonega, Ga.
- Inspector
Where is it found in the NEC which states: All electrical equipment such as receptacle outlets, switches, junction boxes, lighting fixtures, etc. shall not be installed within 6' feet of any ladder attached to the docking facility?
Most of the docks I inspect are bolted to the wood deck boards and no bonded to the frame of the dock in a single-family residence docking facility. The other issues I run into is Article 555.13 All metal parts in contact with the water, all-metal piping, and all non-current-carrying metal parts(such as ladders-me) that are likely to become energized shall be connected to the grounding bus in the panelboard using a solid copper conductor (because of Electrolysis-me), insulated, covered, or bare; not smaller than 8 AWG. Connections to bonded parts shall be made in accordance with Article 250.8 Question: Is this article also used for single-family residence docking facilities?
One more thing, The Corp of engineers at Lake Lanier are trusting electricians to sign off on boat docks around the lake. I often come in afterward and find these safety violations. Is there something in the NEC or Mike Holts videos that deal specifically with residential boat dock requirements I can take to the Corp of Engineers?